Pentair SuperFloVS 1.5HP Variable Speed

Installed this pump about 6 months ago and now it trips the breaker after about 10 seconds. I am not getting any current draw on either hot leg before the breaker trips. The Vfd also briefly flashes error 0021 before tripping. I’ve read this is a faulty computer drive and being this was not installed “professionally” pentair will not warranty. So now I have a 6 month old $1700 pump that won’t run. Anyone out there have this issue with this error similar with this pump? Don’t think I’ll ever purchase a pentair again after this experience.

Reply from Inyo InyoTyler :

Hello,

Error 0021 on a Pentair SuperFlo VS Pool Pump indicates a communication loss or breakdown between the keypad (HMI/display) and the motor control board.

Most common issues are

  • Loose 5-pin connector - Check the 5-pin connector; make sure it’s connected and there is no corrosion on the pins
  • Moisture or corrosion - Check is there is any water intrusion in the drive; typical signs would be actual water or scale buildup from old water
  • Failed drive or keypad - In this case, the only fix is to replace the drive back end.
  • Clogged impeller - Check to make sure there is nothing stopping the impeller from spinning. Remove the 4 bolts attaching and holding the seal plate to the housing, then remove the diffuser and check to see if something is clogging the impeller up.

InyoTyler
Inyo Pools Support Specialist