Pool built in 2005 - original light fixture Pentair Hayward 7883XX, 7843XX R-40 12 volt 300 watt with a halogen bulb. The bulb burnt out so I replaced it with a 12 volt 35 watt LED light bulb from Florida Sunseeker Pool Tone® Color LED Pool & Spa Lights and Bulbs. I used a new gasket, submerged the light housing for a week before reinstalling, and there is definitely no water leakage. No issues with bulb, water leakage, etc.
After a few months, I decided to replace the old Intermatic Remote Control with a Meross WiFi HomeKit switch. While swapping out the switch, I noticed that the original wiring done by the electrician had the 120 volt feed to the Intermatic Remote direct from a regular non-GFCI breaker and was also not wired to the load side of the GFCI outlet that was feed from the same breaker. The switched output then goes to the 12 volt transformer input.
I thought it would not hurt to put the new WiFi switch to the load side of the GFCI outlet. As soon as I turned the breaker on, the GFCI outlet trips. I researched and could not find any issues with using a WiFi type switch with GFCI.
I then did the following to troubleshoot:
- Disconnected the switched output from the WiFi switch feeding the transformer - GFCI outlet trips (just the switch caused GFCI to trip)
- Tried a different GFCI outlet (new one) - GFCI outlet trips
- Purchased a new dedicated GFCI breaker to use for the light circuit only - GFCI breaker trips
I then had the following results:
- Turn on the breaker with transformer input wired to the load side of GFCI outlet, and the GFCI outlet trips
- Wired the transformer to the GFCI breaker, and the GFCI breaker trips
- Disconnected the light fixture wiring from the transformer but kept the input side connected - tried with both the GFCI outlet and GFCI breaker (two separate circuits) neither one trips (issue is not with the transformer)
- Tested light fixture wiring with Fluke meter - no shorts between wires, to ground, etc. Line to neutral on fixture wiring measured out at 5 to 6 meg ohms (note that LED bulb was still in fixture)
Some of what I have read is to not worry about putting the 12 volt light on GFCI - it is not necessary.
Can anyone provide insight on 12 volt lights, LED light bulbs, GFCI protection for these, etc.? Do I just not worry about the GFCI protection because it is 12 volt?